Hey TJ, back to generators I have another question I understand with 220 welders they don’t recommend you use too long of a cord  otherwise you lose a lot of amps is it the same way with the power generator and how long would you suggest not to go over if you know 

Link to comment
https://www.bigmacktrucks.com/topic/71001-sidetrack-area/#findComment-520496
Share on other sites

i stay under 25 foot on both genset and welders. and i also use 100 amp braided copper cable for my power cords. super heavy, but very little resistance to cause power degradation. 

even with welder leads. i go overboard. i use 250 amp cable for under 50 foot, and have 2 100 foot 500 amp rated cables for when i can not get close to the work.

  • Like 1

when you are up to your armpits in alligators,

it is hard to remember you only came in to drain the swamp..

Link to comment
https://www.bigmacktrucks.com/topic/71001-sidetrack-area/#findComment-520499
Share on other sites

See that Bubba we opened up a whole new can of worms speaking up apple pie. Wife is supposed to be bringing me one from San Francisco. I don’t think she’s going to follow through. I’ve been filling up on Christmas candy anyway but the apple pie did sound good..

Link to comment
https://www.bigmacktrucks.com/topic/71001-sidetrack-area/#findComment-520515
Share on other sites

no apple pie rite now. 

 

 

but i do have half a sweet potato pie left from friday.....i try to limit myself to one 1/4 of a pie a day.

when you are up to your armpits in alligators,

it is hard to remember you only came in to drain the swamp..

Link to comment
https://www.bigmacktrucks.com/topic/71001-sidetrack-area/#findComment-520522
Share on other sites

11 hours ago, mowerman said:

I was fixing on locking the generator in my garage and stretching a card to the power box. It’s around 100 feet.

Normally I put the genny circuit into the shed to keep the noise away from the house

100 feet is pretty long and you'll need a lot of cross sectional area on the cable to eliminate voltage drop

Go big and them some for your lead as suggested or if you can run the inlet to the shed were you wanna sit the genny

Ive run big long aerials on cattle stations (ranches) maybe the longest would be 1000 feet but voltage drop makes it pretty dear out the other end

Voltage drop will burn motors out pretty quick so keep any eye on it if you can, 5% is the max by law out here, would assume the states are the same 

Paul 

Link to comment
https://www.bigmacktrucks.com/topic/71001-sidetrack-area/#findComment-520560
Share on other sites

I have always wanted to try rhubarb pie but nobody I know makes it and you definitely can’t get it at any stores or bakery’s…at least none I know of. And yes I have always wanted to try plum pudding and also fig pudding like they say in the one Christmas song. Like where do you even get fig pudding?

Link to comment
https://www.bigmacktrucks.com/topic/71001-sidetrack-area/#findComment-520561
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...